In Reply to: RE: Perhaps posted by E-Stat on November 14, 2013 at 11:34:17:
If you want to use 10 gauge, then take advantage of code and put in 30 amp breakers.
Sorry can't do that if you are planning on using standard NEMA 5-15R or 5-20R duplex receptacles. The maximum breaker size is 20 amp.